The new forums will be named Coin Return (based on the most recent vote)! You can check on the status and timeline of the transition to the new forums here.
The Guiding Principles and New Rules document is now in effect.

Can I wire sockets with 18gauge wire for 40watt bulbs?

fadingathedgesfadingathedges Registered User regular
edited May 2011 in Help / Advice Forum
I have two light fixtures that I am rewiring the sockets on - one four socket fixture and one five socket fixture. I only use and intend to continue using 40watt bulbs. I believe each is wired with a basic 110 jigawatt line. Is the 18 gauge wire I bought gonna do me right? The 16 was much fatter and I didn't like it.

Bonus point question: Can one still buy the rope-style wires, without the asbestos of yore? I'm picturing a modern wire with an aesthetic cord casing - it seems like someone should have done this.



e~ I don't know anything else about my circuit box except that the house is old as balls and probably was at least partially rewired several times.

fadingathedges on

Posts

  • bowenbowen Sup? Registered User regular
    edited May 2011
    No.

    Looks like 12 is the standard for sockets, 14 for lights, and 18 for low voltage lights.

    http://electrical.about.com/od/wiringcircuitry/a/electwiresizes.htm

    bowen on
    not a doctor, not a lawyer, examples I use may not be fully researched so don't take out of context plz, don't @ me
  • fadingathedgesfadingathedges Registered User regular
    edited May 2011
    Let's negotiate until you tell me what I want to hear 8-)


    Seriously though, Google results are telling me different things everywhere I look. Do you happen to have experience with this kind of thing?

    What classifies as a low-voltage light? My lamps run 60watt bulbs.

    fadingathedges on
  • SpudgeSpudge Witty comments go next to this blue dot thingyRegistered User regular
    edited May 2011
    Low voltage lighting is decorative LED type lighting.

    Old house, you're probably not going to live in it for the rest of your life, the next owners may use 60w (or larger) in the receptacle, etc etc etc make the lighting up to code and just use the 14 AWG

    Better safe than on fire

    Spudge on
    Play With Me
    Xbox - IT Jerk
    PSN - MicroChrist

    I'm too fuckin' poor to play
    WordsWFriends - zeewoot
  • bowenbowen Sup? Registered User regular
    edited May 2011
    Everything I've found low power lighting refers to things below 15 watts. So... nothing other than LED like spudge said. And there's a distance limit of 25 feet from the source, though I can't verify that with a good source. It's in the wall though, why do you care?

    bowen on
    not a doctor, not a lawyer, examples I use may not be fully researched so don't take out of context plz, don't @ me
  • matt has a problemmatt has a problem Points to 'off' Points to 'on'Registered User regular
    edited May 2011
    No. It's not negotiable. It's a fire hazard and not to code. It is extremely important that you do it correctly, or don't do it. Electrical wiring is not a place you cut corners.

    Low-voltage usually refers to lighting that runs off a DC supply, 12 or 24 volt. Any standard incandescent or fluorescent bulb you use is going to be 120 volts, regardless of the wattage.

    matt has a problem on
    nibXTE7.png
  • MushiwulfMushiwulf Registered User regular
    edited May 2011
    You are rewiring something like a chandelier? And this is the wire from each individual socket and then up the chain to the box? (Or, if a table lamp, out the base and into a cord cap that plugs into the wall?) What size wire was on there before?

    Mushiwulf on
  • ThomamelasThomamelas Only one man can kill this many Russians. Bring his guitar to me! Registered User regular
    edited May 2011
    No. It's not negotiable. It's a fire hazard and not to code. It is extremely important that you do it correctly, or don't do it. Electrical wiring is not a place you cut corners.

    Low-voltage usually refers to lighting that runs off a DC supply, 12 or 24 volt. Any standard incandescent or fluorescent bulb you use is going to be 120 volts, regardless of the wattage.

    Low-voltage wiring is usually for telecomm, networking, fire, burg, video and access control systems. Electrical sockets, and residential lighting generally doesn't fall into that category. As to why 18 gauge wire isn't a good idea:

    18 gauge wire is rated for about 10 A. What you're proposing will be less then 10 A so on the surface it seems like it should work. Except that the circuit breaker for most lights is going to be rated for 15 A. Meaning it's not going to trip until it hits that point. Which is 5 A over what the wiring itself will deal with. If you're around 12 to 14 A for an extended period of time then there is a chance it will catch fire. This is generally seen as a bad thing. This is why the electrical code sets out very narrow guidelines about what wires you use for what circuit breakers and what circuit breakers get used for what situations. Now you may say "Well I'm never going to go above 40 watts, so fuck it." which is the exactly wrong attitude. If the home passes into other hands, they are unlikely to be aware you cut that corner.

    So it make it brief, it's a fire hazard. Don't do it. The code exists for a reason and the code isn't written by idiots. Follow it.

    Thomamelas on
  • fadingathedgesfadingathedges Registered User regular
    edited May 2011
    Mushiwulf wrote: »
    You are rewiring something like a chandelier? And this is the wire from each individual socket and then up the chain to the box? (Or, if a table lamp, out the base and into a cord cap that plugs into the wall?) What size wire was on there before?

    It's like chandeliers, the wires with the juice poke out of the ceiling when they are taken down. I am wiring 4 and 5 separate sockets on two chandeliers. The existing wire is ancient brittle stuff with rope casing - somewhat like the stuff shown here but very very old:

    PV2BNSTRBUT_main.jpg


    e~ The current wires are very small, I can't tell if they were 16 or 18 gauge inside the casing because they are pretty frayed. The guy who was supposed to be doing this job said that they were only supposed to run 40watt bulbs, and the previous tenant was using 60's in the operating sockets.

    fadingathedges on
  • MushiwulfMushiwulf Registered User regular
    edited May 2011
    18 gauge is fine for that. I haven't seen material insulation (like your picture) at the hardware store, just different colors of thermoplastic (brown, black, a see through gold, maybe white). You may be able to get other insulation types at a specialty store.

    Mushiwulf on
  • fadingathedgesfadingathedges Registered User regular
    edited May 2011
    What about the fires? Does the fact that I am splitting the feed into 4 and 5 lines make it okay?

    fadingathedges on
  • MushiwulfMushiwulf Registered User regular
    edited May 2011
    You are wiring a lamp with, at most 5 sockets. The wire is rated for 10 amps. That is over 1000 watts. Unless you think it is likely someone will put 200 watt bulbs in those sockets, you should be fine.

    Mushiwulf on
  • MetalbourneMetalbourne Inside a cluster b personalityRegistered User regular
    edited May 2011
    Thomamelas wrote: »
    No. It's not negotiable. It's a fire hazard and not to code. It is extremely important that you do it correctly, or don't do it. Electrical wiring is not a place you cut corners.

    Low-voltage usually refers to lighting that runs off a DC supply, 12 or 24 volt. Any standard incandescent or fluorescent bulb you use is going to be 120 volts, regardless of the wattage.

    Low-voltage wiring is usually for telecomm, networking, fire, burg, video and access control systems. Electrical sockets, and residential lighting generally doesn't fall into that category. As to why 18 gauge wire isn't a good idea:

    18 gauge wire is rated for about 10 A. What you're proposing will be less then 10 A so on the surface it seems like it should work. Except that the circuit breaker for most lights is going to be rated for 15 A. Meaning it's not going to trip until it hits that point. Which is 5 A over what the wiring itself will deal with. If you're around 12 to 14 A for an extended period of time then there is a chance it will catch fire. This is generally seen as a bad thing. This is why the electrical code sets out very narrow guidelines about what wires you use for what circuit breakers and what circuit breakers get used for what situations. Now you may say "Well I'm never going to go above 40 watts, so fuck it." which is the exactly wrong attitude. If the home passes into other hands, they are unlikely to be aware you cut that corner.

    So it make it brief, it's a fire hazard. Don't do it. The code exists for a reason and the code isn't written by idiots. Follow it.

    I'm not an electrician.

    But I am an engineer. Listen to this guy. You want to design a system so that the weakest link is what is meant to fail in the case of an accident. In this case, you'd want the circuit breaker to fail before the wire does.

    Metalbourne on
  • MushiwulfMushiwulf Registered User regular
    edited May 2011
    What about the fires? Does the fact that I am splitting the feed into 4 and 5 lines make it okay?


    If you are running each socket with its own set of wires to a central point and then joining them to one wire that runs up the chain to the ceiling, your weak point is the wire running up the chain. It will be carrying the load from all 5 (or 4) sockets. If you want to prepare for the worst case (that someone will try to run 200+ watt bulbs in every socket), you could size that final wire to the breaker (14g for a 15 amp circuit and 12g for a 20 amp). But generally, lamps are wired with smaller wire internally all the time.

    Mushiwulf on
  • fadingathedgesfadingathedges Registered User regular
    edited May 2011
    Thanks everyone, I think I have enough info to figure out what to do. I'll try not to burn anything down.

    fadingathedges on
  • fadingathedgesfadingathedges Registered User regular
    edited May 2011
    Actually - another question.
    Mushiwulf wrote: »
    What about the fires? Does the fact that I am splitting the feed into 4 and 5 lines make it okay?


    If you are running each socket with its own set of wires to a central point and then joining them to one wire that runs up the chain to the ceiling, your weak point is the wire running up the chain. It will be carrying the load from all 5 (or 4) sockets. If you want to prepare for the worst case (that someone will try to run 200+ watt bulbs in every socket), you could size that final wire to the breaker (14g for a 15 amp circuit and 12g for a 20 amp). But generally, lamps are wired with smaller wire internally all the time.

    I talked to my electrical engineer dad and he seemed to think that this was the best plan for my situation. His primary safety concerns were:

    1) Don't shock yourself.

    2) The 'workbox' in the ceiling which structurally supports the fixture and feeds down the wires is sturdy but old - the wires have the same cloth material casing as the ones I'm replacing on the fixtures (though they are thicker and in much better shape). Point is - probably not up to code. I am not capable or willing to address this, so I'm going to pass that on to my landlord and let him worry about it.

    3) The act of joining five wires into one larger wire which I run to the ceiling probably requires a specific technique to do properly.

    How to do?

    Is there a widget that makes this safe and easy? Is there a picture and a list of Do's and Dont's that I can learn from? How many beers should I have first? Googling for it hasn't helped, and I'd prefer a "this is correct" from someone with some experience before I trust a picture.

    Thanks again PA


    e~ Man at Lowe's says "just twist them all together in a wire nut".

    fadingathedges on
  • MushiwulfMushiwulf Registered User regular
    edited May 2011
    Wire nut is correct, just make sure it is sized correctly. They have a sizing guide on the box/bag of wire nuts. I think what you are looking for is the Ideal brand, 452 (Red) WingNut. It will hold 2 to 6 #18 wires.

    Mushiwulf on
  • bowenbowen Sup? Registered User regular
    edited May 2011
    Yeah probably just a wire nut. But it depends where you're joining them. If it's in a wall or the ceiling you'll probably want a small junction box as well. If it's just at the fixture, a wire nut is fine.

    bowen on
    not a doctor, not a lawyer, examples I use may not be fully researched so don't take out of context plz, don't @ me
  • FiggyFiggy Fighter of the night man Champion of the sunRegistered User regular
    edited May 2011
    bowen wrote: »
    Yeah probably just a wire nut. But it depends where you're joining them. If it's in a wall or the ceiling you'll probably want a small junction box as well. If it's just at the fixture, a wire nut is fine.

    Well, if the wire nut is somewhere in the wall, a junction box isn't "you'll probably want," it's code. It also has to be accessible.

    Figgy on
    XBL : Figment3 · SteamID : Figment
  • fadingathedgesfadingathedges Registered User regular
    edited May 2011
    There is a pair of wire nuts dangling from the ceiling out of the existing box, but I'm talking about an in-fixture nut that brings all my sockets together before running to the ceiling.

    fadingathedges on
  • bowenbowen Sup? Registered User regular
    edited May 2011
    Figgy wrote: »
    bowen wrote: »
    Yeah probably just a wire nut. But it depends where you're joining them. If it's in a wall or the ceiling you'll probably want a small junction box as well. If it's just at the fixture, a wire nut is fine.

    Well, if the wire nut is somewhere in the wall, a junction box isn't "you'll probably want," it's code. It also has to be accessible.

    Yeah that's what I figured, I am obviously not a contractor so I couldn't say for certain.

    If he sells his house and someone finds out that it's not up to code he'll probably end up on the hook for the entire house being gutted and redone. Which is fun.

    But yeah, junction box if it's not at the fixture. You'll likely still need wire nuts, and the red one is for 3+ wires, so go with what the other poster said. All in all it's like $15, it's worth it to not have to pay $house.

    bowen on
    not a doctor, not a lawyer, examples I use may not be fully researched so don't take out of context plz, don't @ me
  • Iceman.USAFIceman.USAF Major East CoastRegistered User regular
    edited May 2011
    I can't believe nobody has said this yet, but consult the NEC (National Electric Code). It's not the easiest thing to read though, nor is it cheap, but you should be able to get your hands on a copy from a library or other such resource pretty easily.

    And before anyone says it, yes I am an actual engineer. Not electrical, but smart enough to know it!

    Iceman.USAF on
  • FiggyFiggy Fighter of the night man Champion of the sunRegistered User regular
    edited May 2011
    I am not capable or willing to address this, so I'm going to pass that on to my landlord and let him worry about it.

    Wait a second. Landlord?

    Does he know that you're rewiring part of his property without a licensed electrician? Some landlords freak out when you hang up a picture, so I'd be shocked if this guy gave you the go-ahead.

    If you do this without his say so, and something goes wrong, he can take you to court. If that house burns down and you survive, you're still completely and totally fucked.

    Figgy on
    XBL : Figment3 · SteamID : Figment
  • SoggybiscuitSoggybiscuit Tandem Electrostatic Accelerator Registered User regular
    edited May 2011
    Mushiwulf wrote: »
    You are wiring a lamp with, at most 5 sockets. The wire is rated for 10 amps. That is over 1000 watts. Unless you think it is likely someone will put 200 watt bulbs in those sockets, you should be fine.

    Bad idea. Follow the NEC, do it right the first time. You can save yourself a lot of headaches by doing this.

    Make sure you purchase the correct wire type and size. Remember, the ampacity of the wire has to equal or exceed the current rating of the breaker.

    Here is a pretty good chart for reference http://www.stateelectric.com/formcalc/ampacity.asp . It is highly unlikely you will be able to buy any #18 or #16 THHN at lowes or home depot.

    Soggybiscuit on
    Steam - Synthetic Violence | XBOX Live - Cannonfuse | PSN - CastleBravo | Twitch - SoggybiscuitPA
  • MushiwulfMushiwulf Registered User regular
    edited May 2011
    He is wiring a lamp. There is no wiring going on in the walls.

    NEC Article 400, Table 400.4 Lamp cord, voltage 300, AWG 18-16.
    400.7 Uses Permitted (2) Wiring of luminaires.

    We also have 402.5 Fixture wire, allowable ampacities for 18 AWG, 6 amps.
    240.5(b)(2) Fixture wire shall be permitted to be tapped to the branch-circuit conductor of a branch circuit in accordance with the following:
    (1) 20-ampere circuits -- 18 AWG, up to 15m of run length

    Mushiwulf on
  • SloSlo Registered User regular
    edited May 2011
    Speaking as an electrician here, a lot of electrical stuff will work if you do it below suggested ratings, but you won't notice for a week, a month, or a year a lot of time. Sketchy stuff, especially when it's not even your house and you're playing with stuff that can seriously damage the property.

    That being said, 18 gauge should be ok for the sockets themselves, but you need to be really careful and tie those wingnuts on properly, because if they get loose, you're going to have some issues (Potentially fiery ones). Also: Running wires in parallel like you're suggesting isn't up to code up in Canada, but then again, I'm a bit confused as to what exactly you're trying to do here.

    I'd never try to do something just barely touching the code limits, let alone something beneath them. Electricity is dangerous stuff.

    Slo on
  • bowenbowen Sup? Registered User regular
    edited May 2011
    Sounds like he's making a Y junction of some sort, hence the junction box in the wall. As far as I know, as long as you wingnut it in the junction box, in a wall, you're okay.

    Seems like he's running a length of fire(edit wire, but that is potentially what he's doing) to two different locations. I'm concerned though, because his breaker probably won't trip properly.

    bowen on
    not a doctor, not a lawyer, examples I use may not be fully researched so don't take out of context plz, don't @ me
  • orangeworxorangeworx Registered User new member
    4 years later, has the place gone up in flames?
    Reason I'm asking is because I have a similar situation, I'm basically making a 3 light set up for my balcony, standard E26 sockets with 25W (max 40W) lamps. But I'll be running it out the wall socket rather than ceiling junction box. All the light plug/socket/wire combinations I've found at hardware stores use 18AWG, even the ones I've found at IKEA... so I don't really see the many "words of caution" on this matter. Light bulbs don't take juice like powered tools, low amperage won't heat wires, 1100 watt capacity per hour vs a max of 120W/hr and specifically considering the setup will not always be on. As @Mushiwulf said, it's pretty standard and whoever said parallel connections is not code, it is my understanding that 3+ light fixtures are done this way, not in series certainly.

    Would be interesting to hear from OP, I'm fairly certain he had no issues whatsoever.

  • zagdrobzagdrob Registered User regular
    orangeworx wrote: »
    4 years later, has the place gone up in flames?
    Reason I'm asking is because I have a similar situation, I'm basically making a 3 light set up for my balcony, standard E26 sockets with 25W (max 40W) lamps. But I'll be running it out the wall socket rather than ceiling junction box. All the light plug/socket/wire combinations I've found at hardware stores use 18AWG, even the ones I've found at IKEA... so I don't really see the many "words of caution" on this matter. Light bulbs don't take juice like powered tools, low amperage won't heat wires, 1100 watt capacity per hour vs a max of 120W/hr and specifically considering the setup will not always be on. As Mushiwulf said, it's pretty standard and whoever said parallel connections is not code, it is my understanding that 3+ light fixtures are done this way, not in series certainly.

    Would be interesting to hear from OP, I'm fairly certain he had no issues whatsoever.

    OP probably hasn't had any issues - most people won't.

    The amount of money and work you save is negligible, use 14 gauge.
    Thomamelas wrote: »

    So it make it brief, it's a fire hazard. Don't do it. The code exists for a reason and the code isn't written by idiots. Follow it.

    If you don't know what's code, find out and follow it.

  • fadingathedgesfadingathedges Registered User regular
    @orangeworx Zero deaths!

    After the rewiring I've had many far fewer bulbs burning out too - but my place is old and anything would have been an improvement.

    I was trying to accommodate the space in an original antique fixture and the thinner wires worked out for my needs - but still, I'd have to agree with @zagdrob that you shouldn't do anything less than standard if you're starting a project and have the option to just be smart.

  • H in OHH in OH Registered User new member
    @orangeworx I was trying to accommodate the space in an original antique fixture and the thinner wires worked out for my needs - but still, I'd have to agree with @zagdrob that you shouldn't do anything less than standard if you're starting a project and have the option to just be smart.
    This thread still has not resolved what really is the code for inside a lamp fixture. True, 14 or 12 AWG is the way to go in the wall, but this is a light fixture. All of the light sockets with 1/8ips threads seem to be designed for 18AWG wire, and if you open a UL listed lamp, you will find 18AWG wire inside. As the OP noted, it is not easy to pull multiple parallel pairs of 14AWG wires through lamp arms. The NEC also limits the number of conductors in an enclosed space.

    Where you can get into trouble is not just if someone puts 200W bulbs in every socket, but if a hot wire breaks and shorts back to ground. The current will rapidly rise until the breaker trips. Your wire had better handle that current beyond the breaker's trip point.

    I would throw in a curveball of the wire temperature rating as well. I recently picked up a waterproof lamp socket for a project. There are surprisingly 14AWG wires built in, instead of teh usual 18 AWG. However, the rating on those wires is TW, which translates to 60 degrees C and maximum 20A current. Looking at 18AWG wire in some lamps, it is all rated TEW for 105 degrees C, or 18-20A max current. That should be enough to trip a 15A breaker before the wire catches fire.

    References:
    IEWC Suggested Ampacities
    Cooner Wire Amp Chart
    ee.nmt.edu/~wedeward/EE382/SP02/current_capacity.pdf

    Thanks,
    --H

This discussion has been closed.